Test at manifold
 
Yes as there should be a rubber oring sealing them in as there designed for use with or without meters

Yes prvs need removing before test
 
Yes as there should be a rubber oring sealing them in as there designed for use with or without meters

Yes prvs need removing before test
Cheers mate. At least I’ve got some information to answer there demands. They want it tested to 5 bar for 24hrs. This may be my last day I think lol
 
Last edited:
4 story building.
I would be testing to 5 bar at or from the top floor.
If the manifold is on the ground floor, you will need 2 - 3 bar to get the water to the top floor.
Just test the system to 10 bar and be done with it and cover yourself
 
Is pressure testing MLCP not similar to plastic pipe, in that the test pressure should be reduced compared to hard pipe like copper etc..
 
Is pressure testing MLCP not similar to plastic pipe, in that the test pressure should be reduced compared to hard pipe like copper etc..

Most plastic pipes want it testing at 10 bar ?
 
I would be wanting the approved plans/tech drawings with sizes on. I wouldn't be making any decisions.
Sure enough you could work it all out yourself but that makes you 'the responsible person' doesn't it?

As you said, beyond the pay grade! Outside the remit!
 
Most plastic pipes want it testing at 10 bar ?
Just done my water regs course and it noted that plastic pipe can deform if tested at too high of pressure. 1.5 times max operating pressure is the norm for hard pipe, plastic pipe should be tested at 1.1 times design pressure.
 

Attachments

  • IMG_4185.JPG
    IMG_4185.JPG
    437 KB · Views: 13
Just done my water regs course and it noted that plastic pipe can deform if tested at too high of pressure. 1.5 times max operating pressure is the norm for hard pipe, plastic pipe should be tested at 1.1 times design pressure.

Was reading what hep want they want a test pressure of 18 bar

if any of our slimline fittings are included with the system, then an 18 bar test for minimum of 45 minutes should be carried out.(the old grey ones)
 
Some conflicting information there then, 18bar sounds pretty excessive though doesn’t it. Just looked up the JG speed fit test method and it states 2bar for 10 mins and 1then bar for 10 mins, maybe it’s this short time period that prevents damage?
 
It’s weird would stick to 1.5x myself saw on jg website there fittings and pipe are tested to 44 bar (under lab conditions) so can’t be too bad for them
 