Messages
28
Vaillant ecomax 18e boiler noise at cold start.

Replaced heat exchanger with reconditioned unit and new flue collector as kettling was getting problematic. Works fine except vibrating for around 10 seconds on cold start. Didn't do it before. Any ideas?
 
Are you the homeowner?
 
Get the gas engineer to loosen the case mounting hex bolts 1/2 a turn
 
He should of checked it

I suspect the bolts are tight vaillant did a tb a few years ago saying you need to loosen then and install copper grease due to problems with noise I’m guess as it was second hand it didn’t come with this information
 
Heat exchanger mounting bolts
 
Unable to track down the tb but have had a response from vaillant. The grease is to stop creaking and clicking noise which isn't the problem but the spec for tightening the nuts is only 6nm which I guess he overtightened with the water pump pliers he used. I noticed he also didn't replace the nuts with the new ones supplied with the flue collector. Not sure if that's important enough to get him to change when he loosens them.

Many thanks for your help. I'll post the outcome.
 
Unable to track down the tb but have had a response from vaillant. The grease is to stop creaking and clicking noise which isn't the problem but the spec for tightening the nuts is only 6nm which I guess he overtightened with the water pump pliers he used. I noticed he also didn't replace the nuts with the new ones supplied with the flue collector. Not sure if that's important enough to get him to change when he loosens them.

Many thanks for your help. I'll post the outcome.
Boiler now much quieter. Plumber loosened heat exchanger clamps slightly which helped but richening the gas mixture from 8.1% to the specified 9.1% seems to have resolved it many thanks to shauncorbs for his advice
 