Bonding present and before and tees, but not within 600mm from meter.

Discuss Bonding present and before and tees, but not within 600mm from meter. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Matt0029

Gas Engineer
Messages
1,143
As the title how would people report this on a Cp12? The bondings present, visible and before any tees. However its is not within 600mm of the meter. Thanks.
 
Supposed to leave a bonding notice informing responsible person. I would note it down in your notes section. Unsafe situations procedure mentions it as does TB102.

Are you not able to move it?
 
Supposed to leave a bonding notice informing responsible person. I would note it down in your notes section. Unsafe situations procedure mentions it as does TB102.

Are you not able to move it?
Would need an electrian to join on to the clamp where it is presently and extend I would of thought. Not enough slack for me to move it. Its around 1.5 to 2 meters from the meter.
 
Would need an electrian to join on to the clamp where it is presently and extend I would of thought. Not enough slack for me to move it. Its around 1.5 to 2 meters from the meter.

Not sure it can be extended anymore, I’ve been told by our sparks it has to be a continuous loop. As it has been advised by others it appears to be ok as it’s before any branch :D
 

Reply to Bonding present and before and tees, but not within 600mm from meter. in the Plumbing Jobs | The Job-board area at PlumbersForums.net