Boiler losing pressure

Discuss Boiler losing pressure in the USA Plumbers Advice area at PlumbersForums.net

Messages
2
Hi,

I own a Valient ecoTec boiler combi boiler which is located in the loft.

I am losing water pressure daily but am at loss as to what is causing it.

During the day, when I pressurise my system to 1.5 bars, it runs for 8 hours before losing, any pressure.

In the evening, once I pressurise it, it runs for about 20 mins before it loses pressure.

I have no rads in the loft, there are no water marks on the ceiling of the ground floor so the system is not leaking on the first floor.

I have also isolated the flow / return on the ground floor so no leaks there.

All trv valves have been checked and no leaks.

A gas engineer states the boiler is fine and that I have a water leak. At the rate that I am losing pressure, the leak would have showed up by now.

I am at a loss as to what could be causing it.

I would welcome any advice.

Thanks

Aaron
 
Sounds like an expansion related issue, should be easy enough for any competent person to sort, must be able to work on gas boilers though. Only other issue could be the prv passing, there will be a copper pipe under the boiler that may terminate outside, check if that has water present.
 